how big is too big
heatseeker1
Member Posts: 72
Is a 150,000 BTU gas-fired steam boiler too big for a 1540 SqFt, 2 story row home with 8 baseboard and 1 coil radiators? The system is a two-pipe system, which most of the time is very noisy due to water-hammer. How much sense would it make to have the existing boiler re-piped? The boiler was installed twenty years ago by an engineer, not a heating specialist. I was told that the near-piping was not properly installed. Do you think that re-piping it would cut down on the noise? Thanks for your suggestions.
Heatseeker1
Heatseeker1
0
Comments
-
You can't go by house measurements to size steam boiler, it has to be done measuring the radiators and or baseboard getting a total EDR and size the boiler to that. There are many sites on how to figure out EDR for different types of radiators.0
-
If the near boiler piping is nt right you are probably getting wet steam, if the slope of the piping is wrong and there is water trapped in the piping that will cause water hammer when the steam comes across sitting water in the pipes.
Make a list of all of your radiators and find one of the radiator EDR charts so you will know what EDR each one has, add them all up and that will tell you what size boiler you should have. The boiler name plate lists sq ft of steam as well as BTU's, the boiler sq ft of steam should be close to the total of all your radiators. If the boiler is too large it will be somewhat inefficient but it can still provide good quite operation. My old boiler was much to large for my system and it heated the house quietly but was not as efficient as it could have been.
Post some pictures of the boiler and the piping around it. Get a level and make sure the steam mains are pitched so water can find it's way back to the boiler.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
A boiler which is too big -- or much too big -- will waste fuel. No argument. What it will not do, though, is cause hammering. Bad piping -- near boiler or out in the system, will do it every time.
As has been said, one of the first steps is to check the near boiler piping. Is it correct? According to the manufacturer's specs? if you can, take some pictures and we'll comment on it. Second, check all the steam pipes and any returns for proper slope. All of them, and every foot of them.
Third, make sure the pressure on the boiler is low enough -- pound and a half, max.
Then begin to worry about finer issues -- such as the size of the boiler, adequacy of venting, etc.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
If the boiler is oil fired, or at least has a gas burner, then this can be down fired. The piping above the boiler is at least as important in making a system silent and even, so let's see some pictures.--NBC0
-
Our house is just under 1700sqft and my boiler is 150K input. It's way too big for the house but fits the system.
I agree with what others have said. Post some pictures of the piping around the boiler if possible.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Thanks to all for your excellent, straight forward advice. I will measure the rads and post a picture asap.
Heatseeker1
0 -
This is the only picture I have at the moment. It only shows one side of the boiler and not the piping above the system. I'll send more as soon as possible.
Heatseeker10 -
That looks like a Dunkirk boiler- it may be have different name on it, but Dunkirk re-brands their boilers for several others.
Whoever installed this boiler did not pipe it properly. These boilers do not tolerate improper piping, and the manual has some very specific diagrams. There are two problems I can see right away:
1- the steam pipe leaving the boiler is bushed down from 2-1/2" to 2";
2- the steam pipe does not rise to a 2-1/2" or larger header located 24" above the boiler's water line.
This boiler needs to be repiped. Where are you located?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Steamhead,
I live in Philadelphia. And yes you are right, this is a Dunkirk!
Heatseeker10 -
I just noticed something in your picture...is that a 16 ga extension cord feeding power to the transformer? If it is yikes!0
-
Good heavens, KC -- it surely looks like an extension cord, and it surely looks like it's feeding the transformer...
Uh... not good, folks.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements