two remote radiators not working
RLS
Member Posts: 4
Two of the more radiators in one pipe steam system either underperforming or not performing at all when all the others on all floors and sides of the building work fine. Three story 1915 Victorian with five year old steam boiler. See attached schematic
0
Comments
-
End of the line rads cold
Is this a parallel flow or counter flow system?
What sort of main vents are on the dry returns if parallel?
Can you try the open vent test? You need a helper to switch off the boiler when steam arrives.
If your pressure is above 1.5 psi, some radiator vents will not work.--NBC0 -
the old rule is...
Vent your mains fast and vent your radiators slow, but completely.
Any combination of slow main vents and fast radiator vents will play heck with even steam distribution, causing the last radiators, to not get steam.
Since you have a new boiler, pictures of the piping connecting to the boiler as well as your radiators and vents would be a great help to those of us who are trying to get a handle on your system and offer sound advice.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
Does sound
like a venting problem. If the air can't get out, the steam can't get in. Check those vents.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements