I have a steam boiler that goes up to five pounds pressure and shuts boiler off for one hour befor it relieves pressure back to turn boiler back on.
0
Comments
-
Need a lot more information to be helpful
but if that's a residential boiler there is something really wrong with the controls. If it were mine I wouldn't operate it until I found out a lot more about it and fixed the problems.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Off on safety for an hour
It is probably not the pressuretrol which is keeping off the boiler for an hour. More likely it is the LWCO, or another safety. A little troubleshooting with a multimeter should show which safety is responsible. When the flame cuts out, the steam collapses, developing a vacuum, which could hold water up in the returns for that length of time, starving the boiler of its water.--NBC0