Copper Joint that leaks in main pipe Solution please
acl10
Member Posts: 349
Can anyone give me a good solution besides changing the pipe. On the main pipe around 20 feet away from the boiler the joint leaks. At that juncture there is alto of water hammer and it keeps cracking the solder. I used 50/50 solder and it still cracked. I asked someone about brazing but he told me you cant mix the two solders. Is there any other way to join the copper pipes or any other ideas.
I really appreciate any comments.
I really appreciate any comments.
0
Comments
-
More pictures please,
I don't type very fast but I'm trying to be the first to ask; could you post pictures of your boiler showing all the piping around it? Also how old is this copper piping installation and is this the only leak you have observed? Others beside me are probably curious.
And more questions; which came first: the water hammer or the leak? Does the pipe sag at this coupling? If so that may explain the water hammer and the problem to trying to re-solder a wet joint with water inside it. If this is the only problem I would cut out the coupling, add a length of pipe with repair couplings or a union. After cutting though, pushing the piping up and down to drain the water out will help the solder take. If it is always flowing then the union has worked as you can raise the pipes up as you solder to keep the water back from your joint. Assuming this is a steam main it should in theory drain all water out when cold. But is all your steam pipe copper? That is the reason of the request for more pictures. All pipes that carry steam are supposed to be black threaded pipe. If they carry only condensate return water then copper would work.0 -
Follow up
The water hammer was there first. This is part of the main. Its in middle of the basement not near the boiler. The most of the main is iron pipe. This section was changed because there was a leak in the iron pipe. I did drain the water when I soldered it because I put a valve in the main to drain the water. Is there some union you can use on copper? It doesn't sag so that's not the problem. I cant do anything about the water hammer. Is there a way to thread the copper?0 -
Copper problems
It would be best to replace the copper with iron pipe., which can withstand the water-hammer which apparently you can do nothing about.
The expansion and contraction with temperature changes of copper pipe is so great as to weaken the joints.
Post some pictures of your boiler and it's piping, and let's devise a plan to cure the water-hammer.--NBC0 -
More pictures
Here are the pictures of the valve to get drain the water and other pictures of the pipe. So far this is the only joint that leaks.0 -
Union
There are copper sweat unions which would put this together, just check one out of any size and it will be self explanatory.(if that is 2" check the price first) And the newer "no lead" solder is susposed to be stronger than 50/50. But with a section of copper between 2 sections of iron this might happen again. With the rate of expansion and contraction of copper being much greater than iron this will push/pull on the joints again; perhaps this is what caused the first failure. I believe that most here would recommend going back to an iron pipe repair with a union. IMHO.--------Looking at the last of 9 pictures you posted you can see the hanger rub marks where the copper is moving as it heat/cools; the iron will not move that much and puts the copper between "the rock and a hard spot".0 -
your torch is too small to fully heat the pipe
and the solder needs to be silver bearing, 50/50 is too soft and the only stuff around now seems to be full of impurities. Copper should not be used for steam piping, but you know that. If you need to fix this I strongly suggest replacing it with iron and finding out the cause of the water hanging in the pipe or you will never be done with this.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
Here are pictures of Boiler piping
Here are pictures of the piping around the boiler although I don't know what I can do at this point.0 -
Water hammer
can generate overpressures quite sufficient to actually break pipe -- never mind joints. I quite agree that the best way to handle this one is to change that copper out and put in iron.
But you say you can't do anything about the water hammer. Why not? Water hammer isn't an inevitable part of any plumbing system -- whether it's residential or 60 inch municipal mains. Don't give up on that -- you control the system, you should spend some time to figure out where the water hammer is coming from and fix it.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
As others have said...
your best bet is to change out the copper steam lines for screwed iron pipe.
That said, for repairs to this failed copper joint, first get a slip coupling for this tube size. These have the inside diameter sized to slip over the outside of the existing tubing.
To install, cut out the failed joint, slide the slip coupling in place and solder or braze the joint.
For a stronger joint, I would look into PHOS COPPER brazing rod. A Google search will tell you all you need to know. You will need to heat the joint to red heat, but the nice thing about Phos copper is it is much stronger, and is self fluxing on copper to copper joints, so you don't need to worry about getting the joints super clean.Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.0 -
What do you suggest
What do you suggest I do to correct the water hammer. I posted the pictures.0 -
One source of your hammering
may be in your improperly piped boiler. Do you have the make & model number of that boiler?
http://www.heatinghelp.com/article/440/Videos/118/Steam-boiler-near-boiler-piping-video0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements