Banging pipes and venting mains
raemac
Member Posts: 14
I have 2 gorton #2 vents on end of 100 ft mains. The seem to open when cold but close when hot even when no steam comes through. This is causing no ventilation for water to flow back into boiler and get stuck in pipes. My installer of new system separated first floor from 2nd and 3rd floor with electric valves that they use in commercial installations. Lots of banging in pipes. My first question is about set up. Does this look correct? Am a I asking for trouble having 2 zones? Should I have more vents in main at different locations?
0
Comments
-
Is this
a one-pipe or two-pipe system?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Steam
Hard to see but it looks like the near-boiler piping is all wrong. Is the banging coming from around the boiler?
Zone valves can be installed with no problems, but they need some special attention.0 -
One pipe but two mains
It is a one pipe system with 2 mains. It used to be 2 separate systems in a two family home that is now a one family home.0 -
If those zone valves
are not dripped on both sides into wet returns, you will have trouble with them. They will hammer -- it's almost guaranteed. Further, if they are not full port valves, you will have even more trouble, as steam will have trouble getting past them (the thermodynamics is messy, but the bottom line is that saturated steam condenses like mad when it goes through a restriction which then opens out again).
As Joe said, zone valves can be done on one pipe steam -- but it is a little tricky.
The Gortons should close when steam hits them. That's what they are meant to do. They will open when they cool a little; that's also correct. They will NOT open, however, if the pressure is too high, so that's something to check. I doubt very much, however, if a closed vent would prevent condensate from draining back. You are not dealing with a full pipe here; the condensate is laying on the bottom, and there is ample opportunity for it to drain back and for air in the pipe -- vent open or not -- to replace it.
On additional vents. Depends a little on where vents are in relation to those zone valves. If there are vents beyond the zone valves, they need to be duplicated on the hot side of the valves.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Zone valves
Thanks Jamie,
I think the zone valves could be the issue.
I may have to have someone come out to take a look at configuration0 -
Lots to consider when using zones on Steam Heat
The system has motorized valves.
http://www.heatinghelp.com/article/95/Problems-that-plague-ALL-steam-heating-systems/80/Theres-water-hammer-in-the-system
The gravity-return system has motorized valves.
http://www.heatinghelp.com/article/95/Problems-that-plague-ALL-steam-heating-systems/90/The-boiler-is-flooded
There are motorized zones valves near the header.
http://www.heatinghelp.com/article/95/Problems-that-plague-ALL-steam-heating-systems/96/The-condensate-or-boiler-feed-pump-doesnt-behave-as-it-should
Zoning steam systems.
http://www.heatinghelp.com/article/326/Zoning/253/Zoning-Steam-Systems
Zoning a steam system? Watch out!
http://www.heat-timer.com/enFiles/News/newsletter6_20100408085351.pdf0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements