Oversized boiler
TonyS
Member Posts: 849
I went to look at a job that was put in a few years ago, its got everything, cast rads in the old section, baseboard fin and radiant in the new. Complete disaster!
The boiler was installed a few years ago also, Burnham cast iron 170k ,its about a 100k over sized. Question is ...How do you guys feel about removing burners to down fire this beast. PROS...CONS AND TECHNIQUES ?
The boiler was installed a few years ago also, Burnham cast iron 170k ,its about a 100k over sized. Question is ...How do you guys feel about removing burners to down fire this beast. PROS...CONS AND TECHNIQUES ?
0
Comments
-
I Wouldn't Do It
Tony,
I wouldn't do it under any circumstance. If you do, you own it and all the ramifications that come with it. It's illegal to modify the gas train in a manner not approved by the manufacturer and AGA. I'm sure Tim can give better specifics.
I'd look at a buffer tank or a properly sized boiler.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Not a good idea for a couple of reasons
1. The overall efficiency will be affected as you still have to heat all the sections
2. Safe ignition can also be a problem depending on what burners are blocked off.
3. It could affect the warranty on the boiler if that is still a factor depending on age
4. Manufacturers of equipment will not authorize such a move.
You can by changing all the orifices to smaller size or adjusting pressure typically reduce input about 10% which is not the best but better than blocking off burners.
In all cases I would do a before and after combustion analysis.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements