Before I soldier this up for the third time, I thought that would ask if someone could take a look and see if have any major flaws with my design. This system is used to heat my garage. The water hear is off to the right. The supply (cold) is on the bottom, return (hot) is on top. The bottom lines feed the in floor radiant heat. This redesign was to add a mixer valve to the radiant zone. The top lines feed two unit air heaters. It is setup as a two zone system, one for the floor, the other for the unit air heaters.
Thank you
Howard
Thank you
Howard
0
Comments
-
Third times a charm
Howard,
It is hard to tell which way the circs are pushing.
Are the 2 left ones pushing left?
If so the right one should be pushing right and connected to the return on the heat source.
It is hard to tell from the picture.
Carl"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
circs
Carl, you are correct about the direction the circs are pushing.0 -
circs
Carl, you are correct about the direction the circs are pushing.0 -
Solder away
I think what you have will work fine
Carl"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
thank you
Carl:
Thank you for your time.0 -
Piping looks good...
But is your radiant floor heat in slab or staple up to a wood floor?
If it's in slab, then you don't want to use a thermostatic mixing valve to control the water temp. The high mass of a slab will cause it to continue to give off heat for hours after the thermostat shuts off. If water temp is not varied by outdoor reset to match the load, the zone will over heat. You'll need a "smart valve" or variable speed injection mixing to properly control the water temp. Injection mixing is better but would require some more re-piping. Look at Taco's smart valve.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements