newbie needs help
timberwolf77
Member Posts: 6
Okay I am totally new to having a boiler. Just bought a house thas about 100 plus years oldand went to turn on the heat the other day and about 15 min later I find my basement looking more like a sauna. Here is a little backround to the story. We found this house and after we put our bid in someone broke in and stole some of the copper. The guy we bought it from had a team of contractors staying here after that till we closed. They replaced the copper. I talked to the contractors one day and they mentioned that whoever stole the copper never turned off the pump so that got replaced to. So now I am having a prob with the heat and I start checking things out. I bled the lines and fired it up again it starts out about 15 psi and starts climbing once the temp gets about 140 the pressure is at almost 30 soon after the valve will pop and there is where the steam comes from. One thing that is confusing me is the pump which is towards your the bottom of the boiler has a flow arrow pointing up which leads to the valves for my 4 zones. But the valves all have arrows pointing down. Could this be the problem? Which one is right?
0
Comments
-
A picture..
Could you post a picture of what you have along with the boiler model?
Is there an expansion tank in your system?
Carl"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
model
Utica 175AGB yes there is an expansion tank.0 -
Backwards
The circulator should be pumping the other way. You should be able to close the green handled gate valves and just flip the circulator over.
I kind of doubt that is causing the pressure to rise that high. I think you have a waterlogged expansion tank. As the temp in the closed system rises the water has no place to expand and the pressure rises. If you tap on the tank , is it full of water?
Carl"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
pump
Yep pump was definitly backwards. Changed it and now pressure stays good. Runs fine. Too bad they did just as bad with the pipes. Found 2 pipes crossed only half the house gets heat.0 -
exspansion tank
Tank sounds fine. Hollow at the bottom.0 -
Glad to here
The circ, expansion tank and the pressure is good.
What is up with the pipes?
Carl"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
pipes
Yep everything else is working good. When the copper pipes were stolen and the contractors replaced them they crossed 2 of the lines to 2 zones. So there was 2 pipes supplying the same zone and 2 returning the same zone. I just got done fixing that now and everything is heated nicely. Thanks for your help.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements