Triple Aquatat RElay
Chris279
Member Posts: 4
I just bought a house and changed the Thermostat to a programable one, before the heat would just be on all the time, now that the new thermostat is in the only way i get hot water is if i bring the heat up above what is on the thermostat, I have a combi Boiler . im looking at the Aquastat and the T T are jumped is there a reason for this or what can be the problem maybe a faulty thermostat? or what ?
0
Comments
-
More info
You really need to post the model of the boiler and a diagram of how it is wired."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
-
wiring
What is your thermostat connected to ? Do you have more than one zone? With TT jumped on your aquastat the boiler will be up to high limit constantly and the heat will always be on. It is not correct, and it is not good for economy. It needs to be fixed. There may be something wrong with the aquastat also.
I also see a valve between the domestic hot and cold water pipe near the coil. This valve must be closed. It also should not be there. It is a misguided attempt to meet the requirement for a tempering valve. You really should have a thermostatic mixing valve installed.
Some one who is familiar with this control should be able to sort it out very quickly but it does need professional attention0 -
Re
I bought the house and this was in there I know it has only one zone, so in other words should I disconnect the jumper wires ? And what else0 -
Wiring cont.
I cannot tell from the photo but appears that there is no neutral wire (line 2) at the L1 L2 connection of your 8124 aquastat control. The control may not work correctly with out that wire on L2. It appears that the LWCO wires are junctioned together inside your aquastat. The red wire may be obstructing the relay clapper.
This whole mess should be rewired by some one who knows what they are doing. There may be some real safety concerns here.0 -
For starters......
Your low limit is set too high. The thermostat needs to be wired to T-T on the aquastat. The jumper on the primary control is fine.
But you should have the system checked out, completely troubleshooting the triple aquastat. It's also possible somewhere in that wiring mess something is mis-wired or a loose connectionThere was an error rendering this rich post.
0 -
look in the manual
Do you have the manual for that boiler? Follow the wiring diagram in the manual and see what is different with the way this is wired. If you don't have a manual you can download one here (I think this is your boiler) look under the downloads tab
http://www.williamson-thermoflo.com/en/williamson/pd-owt-oil-water-boiler-tankless/
It sounds like something is miswired, the guys who have responded do this for a living so if you can explain how it's wired they will know how to fix it.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Long Island?
Do you have 120v thermostat? Very common on LI.To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
Long Island
Yes I am from Long Island I really don't know much about this wiring0 -
LI
It's a 120V thermostat, needs to be rewired and very often there aren't two dedicated wires to thermostat and it requires a RIB relay. Very common here on LI,almost unheard of elsewhere,at least we have good pizza!To learn more about this professional, click here to visit their ad in Find A Contractor.0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements