wiring a control
Duff
Member Posts: 61
in place on an oil fired boiler is a L8124C aq controller and all the relays are honeywell RA89A.One of the 89A relays are wired to the L8124 on the TT and the CC terminals !!!! This boiler will only go to high temp when that zone is calling for heat
I'm not sure if the 89A can stay in place? Can't find any wiring diagram with the L8124 and a 89A. All diagrams are showing a RA845. This installation does have a indirect storage tank for DHW.
The ZC and ZR terminals are not connected.
I may have to just add a taco 505 relay and do away with all the 89A relays
Anyone got any ideas???
Thanks in advance, Duff
More Details
Do you have zone circs or zone valves(2 or 4 wire)? How many? I assume you wired the aquastat the same as he old one? The 89a is pretty limited.
Albert Einstein0 -
hi Zman
4 cirulator zones, 3 for heating and one for DHW.for a storage tank.
Yes I wired the new L8124C the same as what was there. I thought the relays were R845 so was gonna use the ZC and ZR but when I pulled the cover from the relay my whole idea changed.0 -
504-4
Bummer,
I would scrap the individual r86 relays and put in the Taco 504-4. It will allow DHW priority if needed.
Albert Einstein0 -
thanks Carl
I agree with you, thanks for getting back to me. I sent Honeywell an e-mail with my question and I'll let ya know what they have to say when and if they respond.
The taco box is the right move, there haven't been any upgrades on this job for 15 years so it's long overdue, Thanks again for the help,
Duff0