Radiant floor heat source using GeoSpring hybrid water heater ...anyone doing this?

0107
0107 Member Posts: 6
Currently using a standard water heater for a radiant floor heat source, ~100F set point.



Thinking of moving to GeoSpring.



Anyone see an issue with this?

Comments

  • HDE
    HDE Member Posts: 225
    I see a lot of problems

    It's a hybrid heater using a 550 watt heat pump with 2 -4500 elements.

    If you leave the elements active they will be on most the time. If that's the case a standard electric water heaters 1/4 the cost.

    The heat pump compressor is only 550 watts so it will only produce about 1,900 BTU's. while in operation it will produce cool air that may need to be reconditioned cutting into your net output.



    In most cases 1,900 BTU's would barely heat 50 square feet and less.



    Leave the elements on and you may have a total of 17,000 to 19,000 BTU's total which isn't much more than a plain electric.



    In the end 1/2 the BTU's of a standard gas tank, not much more than a electric, expensive probably to operate to receive less than 20,000 BTU's.



    A condensing boiler hands down for efficiency would be better, especially against the cost of a hybrid tank.
  • Jamie Hall
    Jamie Hall Member Posts: 24,110
    Heat pumps

    don't add up power in quite the way resistance heating does.  The 550 watts used to power the compressor does not equate to 1900 BTU but to considerably more (as much as 3 to 4 times more, in some situations).  The exact amount more, unfortunately, depends on such details as the temperature of the air available to the evaporator section.



    I would recommend a thorough evaluation of the demands and operating modes of the unit before stating whether or not it would be a good fit.  It might be.  Then again, it might be necessary to run the resistance elements, which would send up the operating cost.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Zman
    Zman Member Posts: 7,609
    edited January 2013
    The heat comes from the house.

    The geospring pulls energy from the air around the heater and puts it in the tank.

    I don't see what you would be accomplishing.

    Carl
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
  • HDE
    HDE Member Posts: 225
    Can't believe I said that

    Posted before coffee



    But with a COP of 2-4? What the heater worth about 5-6 KW ?
  • kcopp
    kcopp Member Posts: 4,462
    really...

    the room that the heater was in would be freezing.
  • Zman
    Zman Member Posts: 7,609
    Yes

    The heatspring does not have anything mounted on the outside of the building, Yes?

    That leaves 2 options;

    It is pulling the heat from the air in the house.

    It is running on magic.

    It is a heat pump. Where is the heat coming from?

    Carl
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
  • SWEI
    SWEI Member Posts: 7,356
    pulling heat

    Works really well in Hawaii and Florida - the HPWH provides a free space cooling enhancement.  For the rest of us, I've always wondered if someone made one with air duct fittings so we could install a summer/winter switch (damper.)