2 pipe direct return
JBol
Member Posts: 3
My friend got himself in trouble ripping out his 2” cast boiler mains and replaced with ¾” copper supply/return mains. Now only first radiators get hot on each of two loops. I bled every radiator until I got water and the system runs quiet, convinced theres no air. Closed the balancing valve on the first rad, and second one got hot. Second rad has no balancing valve. Also his headers are bushed down to 3/4” before they bullhead to the two branches.
Here’s all the details I can think of…
Cast iron gas boiler at least 50 years old, 137000 btu input
Two pipe direct return ¾” mains
2 loops split front/back of house, 2 story house
5 radiators on front loop, 6 rads on back loop
no balancing valves upstairs, balancing valves on first floor radiators only
circulator on boiler return pumping away from exp tank
headers bushed down to ¾” before branches split on bullhead tees
lastly, system used to work with 2” mains! Too late to go back.
The fundamental problems I see are lack of balancing valves on a 2 pipe system, and undersized headers. The system could benefit from a boiler bypass as well, no?
Are monoflow tees ever applicable on a 2 pipe system? Any other advice?
Thanks for anyone who can help.
Jesse
Here’s all the details I can think of…
Cast iron gas boiler at least 50 years old, 137000 btu input
Two pipe direct return ¾” mains
2 loops split front/back of house, 2 story house
5 radiators on front loop, 6 rads on back loop
no balancing valves upstairs, balancing valves on first floor radiators only
circulator on boiler return pumping away from exp tank
headers bushed down to ¾” before branches split on bullhead tees
lastly, system used to work with 2” mains! Too late to go back.
The fundamental problems I see are lack of balancing valves on a 2 pipe system, and undersized headers. The system could benefit from a boiler bypass as well, no?
Are monoflow tees ever applicable on a 2 pipe system? Any other advice?
Thanks for anyone who can help.
Jesse
0
Comments
-
bump
I am doing the above job this weekend. Was hoping for some answers so i can get the right parts and plan accordingly. In need of heating help! Thanks...0 -
If the system worked well before
ripping out the 2" mains will tell you that whatever your friend did was wrong, no?
That 3/4" pipe will eventually ruin the boiler because there's not enough water flow to absorb all the heat being created in the heat exchanger. Your boiler is probably complaining already. In addition, 3/4" pipe will only be able to heat maybe a third of the radiators in the house.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Sounds almost
as though this may have been a gravity system at one time? With the big mains? It may be very difficult indeed to get it so that it's even remotely balanced without going to primary/secondary and zone valves or zoned pumping. And more flow through the boiler...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Btus
I would think he could get 80,000 btus out of two 3/4 loops. The boiler can probly only output 100,000 so it's not that far out right? My biggest concern is how will balancing valves affect the btus the loops can draw....0 -
Gravity Systems
You might benefit from Dan's article on gravity systems found under the "Systems" tab above:
http://www.heatinghelp.com/article/332/Gravity-Hot-Water-Heating/72/Gravity-Hot-Water-Heating-FAQBob Boan
You can choose to do what you want, but you cannot choose the consequences.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements