Ignitor not glowing on demand for heat
pattymac
Member Posts: 1
in Gas Heating
Sequence of events
Thermostat calls for Heat
Hear click
Blower starts
Nothing else
Thermostat fine
New Igniter Flame Rod Assembly
Pressure Switch seems fine
Check voltage at gas valve on demand is only reading 13 volts - ?why not 24???
No wires are broke
Any ideas on where to go from this point to find the problem would be greatly appreciated.
Thermostat calls for Heat
Hear click
Blower starts
Nothing else
Thermostat fine
New Igniter Flame Rod Assembly
Pressure Switch seems fine
Check voltage at gas valve on demand is only reading 13 volts - ?why not 24???
No wires are broke
Any ideas on where to go from this point to find the problem would be greatly appreciated.
0
Comments
-
Need more information
Is this a furnace or a boiler?
Make and Model number of gas valve, module etc.
Thermostat fine
New Igniter Flame Rod Assembly when was this installed and why?
Pressure Switch seems fine How do you know did you check the differential pressure across the switch? If the blower (combustion air blower) is running it could be the pressure switch is not switching over to power the system for the pilot to light and the burner to come on.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements