Spark Ignition
Johnnyboy
Member Posts: 6
in Gas Heating
I have have an old furnace with intermittnent spark ignition.No inducer fan.When there is a call for heat the spark lights the pilot and the the main burners light and after a few seconds the burners shut down.Sometimes it takes three or four attempts to stay lit and then the heat cycle continues normally.Sometimes the spark process goes three or four times and doesn't lite at all.And sometime after the burners lite and the blower motor is on the spark will continue.Help.
0
Comments
-
The pilot may need cleaned and the
sensor rod cleaned with a piece of soft clean emory cloth.
Are you a technician? The reason I ask is so I can know what direction to have you go next.0 -
Spark ignition
I have technical school Training for HVAC.0 -
Spark ignition
I have technical school Training for HVAC.0 -
sparkm ignition
doen't have a flame sensor rod.0 -
Answers in an hour?
Can anybody help me with my Intermitent spark ignition problem?0 -
Give a list of the control numbers
seeing as there is no flame rod then all the spark does is light the pilot (pilot relight) the flame has to prove some other way.0 -
Jonnyboy be patient
You want super quick answers but are not giving enough information. Your fortunate Tim is taking the time to help you. Listen, then you can get to the bottom of the problem. Take a picture if you can. It does sound like a pilot re lite, but what brings on the gas valve???
Mike T.0 -
Problem solved
I changed the pilot assy and now the furnace works properly.Apparently the pilot flame bridges the gap between the electrode and ground.Thats how the flame is proved.The old pilot assy was not set properly.Thanks anyway.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements