boiler venting
paul_79
Member Posts: 91
in Gas Heating
tim i wrote a while ago about a argument a co-worker and i had about venting the boilers which have been operating ok for 20+ years, he thinks there should be barometric dampers. i say they have been working leave "em alone. They are rite 1.5 million btu. water tube boilers with webster powerburners hot water system. photos show they connect to same flu.
They fall under
the ANSI Z83 standard for Industrial Boilers and do not need draft hoods, barometric they develop sufficient power to vent without assistance. This is typical for many industrial boilers.
I will see if I can find the actual code section in Z83 for you and print it here, IF I can find my Z83 code???0 -
boiler vent
thanks tim i figured the mechanical company twenty years ago knew what the rules were and did it the correct way. thanks for the information0 -
Cross TEE
The vents should of been in a Y configuration to prevent combustion gases from pushing through the other non-firing boiler or even when both boiler fireing. Our code does not permit that type of connection and AHJ would shut it down! Barometrics are not needed as per the boiler's certified I&O depending on site conditions.0 -
Yes Henry you are correct I did
not really look at the pictures that closely. The vents need to be relocated so they are not firing at one another, that is also a code violation in the USA.0