Steam trap return gets hot
Fizz
Member Posts: 547
I have a Richardson system(2 pipe orifice returns), but several(3) rads were added to system, with traditional traps. One of traps gets hot in return when steam gets to trap. Trap is original Trane B-1, integrated cage/seat, which was in dis-repair, i replaced workings with B& J, but it will get hot in return when system has been running a long cycle. Is this normal?
0
Comments
-
How hot is hot?
It would be quite normal for it to get as hot as 200 -- maybe even a little bit hotter. It should not get as hot as say 207. But... my hands, at least, have some difficulty distinguishing the evel of "yeouch" at that temperature. Do you have access to an IR (no-contact) thermometer?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Access to therm
No i don't but I could get one at local plumbing supply store. Thanks.0 -
IR Thermometer
Home Depot has them in their tool dept. . I have a Ryobi Model RP4030 and have been very happy with it. Be sure to take the measurements up close as there farther back you are, the larger the sampling area. Measure the inlet side and the outlet side of the trap and with a properly working trap, you should see a noticeable difference.
- Rod0 -
IR therm
Good advice. Thanks.
Fizz0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements