Which Model Vaporstat for 1 Pipe Steam ?
Rod
Posts: 2,067
Hi- Other questions on Vaporstats reminded me of a question I've wanted to ask. I'm using the 0-4 PSI (1017) model for my 1 pipe steam system and have been very happy with it's operation.
What I am wondering is how many people are using the 0-16 ounces (L408J1009) model for 1 pipe steam and what your impressions are and whether you feel that the 0-16 ounce model is the best choice of the two?
- Rod
What I am wondering is how many people are using the 0-16 ounces (L408J1009) model for 1 pipe steam and what your impressions are and whether you feel that the 0-16 ounce model is the best choice of the two?
- Rod
0
Comments
-
I would rather
have the 0 to 4 for one pipe steam, as it is quite normal for one pipe to need to go to 1 to 1.5 psi at times, and the 0 to 4 variety is just fine for that. Also, IMHO, for most two pipe -- but not for vapour, where you definetly need the 0 to 16 ounce; the system I superintend, for instance, cuts out at 6 ounces and back in at half an ounce...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I am happy with the 0-16
I am using the 0-16 model to control an oversized boiler. The boiler is rated for 500 EDR, I have 377 connected. The vaporstat I have, came from the factory set to: on at 3 ounces, and off at 8 ounces. I left it set to the factory specs. It has been reliable for two seasons now. So far this season, the weather has been mild, my pressure has rarely got up to 8 ounces. The vaporstat did have to work a few times this year when a window blew open and chilled the thermostat. The open window thing has happened a few times, when it happens the vaporstat saves the day. Each time the boiler runs normal for a bit, then cycles off at 8oz, on at 3oz until the window is closed. For me, 8oz is enough, you might need more, or less.
What are you currently set to? How often do you get there? What is your normal operating pressure?0 -
0-16 oz here
running a 0-16oz here on 4 boilers, set to about 4 cutin and 12 cutout depending on the building. I've adjusted some up/down. The only time I'll see pressure get above 1 psi is in the morning when building is recovering from a 3 degree setback.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 919 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements