Trane inducer dilemma
woodheatguy
Member Posts: 7
in Gas Heating
Hi I have a
Trane xv-90 set up for propane. Model # uy060r9v3v. It is about 12 years old.
About 10 years ago my toddler son put the hose in the outlet pvc pipe on the
furnace.(yes he is still alive). I heat with wood and use the furnace fan to distribute
the wood stove heat around the house. Ever since the “water” incident I have
been having inducer motor problems, 3 flashes.If I jiggle the wires or tap on
the motor housing I can get it to work. I only need the furnace part when we
are on vacation or when it is really cold. Last night it was -3F so in the
morning I put on the furnace to help out the wood furnace and all my tricks did
not work. I was looking at the Service facts and saw a thing called the draft
inducer trouble shooting manual. Where can I find this?
I think
since the motor comes on and works fine when it does work there might be
corrosion in the wiring harness. What about the high and low pressure switches
or the inducer housing limit switch. Would any of them give me an inducer error?
Is there any way I can test the motor to be sure it works.
Any help
would me great.
Thanks
Erich Ruger.
Trane xv-90 set up for propane. Model # uy060r9v3v. It is about 12 years old.
About 10 years ago my toddler son put the hose in the outlet pvc pipe on the
furnace.(yes he is still alive). I heat with wood and use the furnace fan to distribute
the wood stove heat around the house. Ever since the “water” incident I have
been having inducer motor problems, 3 flashes.If I jiggle the wires or tap on
the motor housing I can get it to work. I only need the furnace part when we
are on vacation or when it is really cold. Last night it was -3F so in the
morning I put on the furnace to help out the wood furnace and all my tricks did
not work. I was looking at the Service facts and saw a thing called the draft
inducer trouble shooting manual. Where can I find this?
I think
since the motor comes on and works fine when it does work there might be
corrosion in the wiring harness. What about the high and low pressure switches
or the inducer housing limit switch. Would any of them give me an inducer error?
Is there any way I can test the motor to be sure it works.
Any help
would me great.
Thanks
Erich Ruger.
There was an error rendering this rich post.
0
Comments
-
Condensate
There is a pressure switch on the furnace that's "proves" the inducers function and sends a signal to the board.
The # 1 cause of pressure switch errors on a 90% furnace is condensate backing up due to a plugged drain.
There is a trap in the condensate line that will get plugged with debris.
What is 3 flash on that furnace? Usually the chart will be more specific then just pressure switch.0 -
What is the make and number of the
board? That way I can diagnos the 3 flash code.0 -
I looked up your unit
which I believe may be a two stage unit using a White Rodgers 50A50 series board. The 3 flash code is an indication of a pressure switch error. There are two pressure switches on the unit. If the inducer got water in it long ago it might have corroded to the point that it is not able to get up to full speed and pull in the pressure switches. Or as was posted already check the condensate lines. When was the last time this unit was taken apart and cleaned?
Do you have two pressure switches on your unit? I really need the number of the White Rodgers control to get an exact diagnosis.0 -
update
I will get the # off the board in the am. there are a high and low pressure switches . when there is a call for heat , I get no action on the fan at all just 3 flashes that indicates an inducer error in my owners manual. I have never taken out the pressure switches.
is it hard?There was an error rendering this rich post.
0 -
update #
White rogers 50A61-605
Hope this helps
Thanks.
Erich.There was an error rendering this rich post.
0 -
On a call for heat
see if you have 120 VAC from Inducer Lo (pin 3) to Inducer N (neutral) (pin 4) if you do and the inducer is not running the inducer needs replaced At the same time check Inducer Hi to Inducer "N". if there is power on either one of these and the inducer is not running then the inducer is bad.
Just one thing tricky however there is a TCO Thermal Cutout Switch in the Neutral leg from the inducer if you have the diagram for the unit it is labeled TCO-C if that is open the inducer will not work.
If you have a FAX number I can send you some info to help you out.0 -
Fax #
Sorry but I don't have a fax # is it possible to send it as a file attachment to an email?There was an error rendering this rich post.
0 -
Yes
my e-mail is gastc@cox.net, I will get it off to you tomorrow afternoon if I get your e-mail by then.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements