Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Aquastat L8148B

darrind66
darrind66 Member Posts: 1
I have power coming in, power going out to the circulator but no power going to the burner control when there is a call for heat?

Comments

  • heatman101
    heatman101 Member Posts: 19
    Is this a brand new install...

    or is it a control that has stopped working after a period of time??



    The relays are separate and one could be working, but not the other...
  • Ironman
    Ironman Member Posts: 7,555
    Also...

    Could be the limit's open. What's it set for?
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • Tim McElwain
    Tim McElwain Member Posts: 4,642
    The L8148B is

    a isolated burner circuit B1/B2 for use with a powerpile system there is no power at B1 and B2 until the pilot is lit and the pilot generator provides 750 Millivolts.



    So the question what is the status of the pilot?
This discussion has been closed.