Taco 5000-2 Mixing Valve

I'm currently installing this mixing valve on a DHW line at the water heater and I can't get the water temperature above 100 degrees.  I've followed the instructions and I'm on my second valve with the same results.   I've taken the valve apart and it's clean.



Any ideas?



Alan



Edit:  I've followed the instructions except I've not installed a "flow control".  Is this the problem?  I can control the flow at the faucet and even at low flow rates, I can't get an increase in temperature.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

Two btu per sq ft for degree difference for a slab

Comments

  • hot_rod
    hot_rod Member Posts: 23,390
    tank output temperature?

    and what about the cold supply temperature? Check the spec there is usually a min. temperature between hot water inlet and mixed water outlet temperature for the valve to work properly.



    Is it a tankless heater or ?? Mixers and tankless don't always get along so well.



    No lead body, of course for CA.



    hr
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Jean-David Beyer
    Jean-David Beyer Member Posts: 2,666
    Hot supply must be 25F hotter than mixed output.

    For the 5120 Taco valve, the hot supply must be 25F hotter than the mixed output.

    I have another mixer valve (Lawler) whter the hot must be 15F hotter than the output setting. Neither of these seem to specify how cold the cold supply needs to be, but it must be quite a bit below the desired output setting. I would guess at least 10F below.



    Most small sized valves like this need at least 1/2 gpm flow rate to regulate temperatre properly.
  • This is a

    tank-type water heater. 



    The spec's. on the mixing valve are:

    Maximum hot water inlet temp. - 210 degrees (actual is 140-150)

    Minimum cold water inlet temp. - 39 degrees (actual is 45-50)

    Outlet water temp. range: 85 - 150

    Minimum temp. differential (between hot water supply and outlet - 20 degrees
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • All is good!

    As it turns out, there is no problem with the mixing valve.  I had forgotten to install a check valve in the Taco X-Pump Block, cold water was flowing up the return, through the XPB, up the supply and reducing the temperature of the hot water going into the mixing valve.



    Thank you Hot Rod and JDB for your time and your help.



    Alan
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • hot_rod
    hot_rod Member Posts: 23,390
    more about mixers

    Tune in July 21 at noon CST. Julius Ballanco, engineer extraordinaire will host our webinar on thermostatic mixing valve use and piping. When you pipe a recirc into a 3 way mixer there are some important details with check valves, bypass and balancing that is important to assure accurate mix temperature conditions.



    hr
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Hot Rod

    Where is this Webinar?  Could you post a link?

    Thanks

    Steve

    There was an error rendering this rich post.

  • World Plumber
    World Plumber Member Posts: 389
    Webinir

    Try this link. Join the neighborhood and John will send you invitations to join. I took to liking them.



    http://flopro.taco-hvac.com/index.html?action=pr_login_fp#
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    oh flo-pro

    Didn't know it was Flo Pro. Thanks, I already joined...

    There was an error rendering this rich post.

  • MikeyB
    MikeyB Member Posts: 696
    Webinar

    Check out Caleffi's Website for Hot Rods Webinars
This discussion has been closed.