Is this do-able?
Kestrel
Member Posts: 102
Trying to figure out if retrofit, joist-space radiant floor installation will meet heat needs.
Huge help from Brad White last week on heat losses. The question concerns a large, mostly open first floor, to which I have access to joist space in context of basement remodel (building 'man-cave' for teenager/friends/guitars/XBox/etc)
So, about 700 ft sq main floor, with about 579 ft sq available for under-floor install (reduced by cabinetry, up and down stairs, etc). Heat loss for total area 18500 BTUH at design temp of 20'F here in Seattle, or 32 BTUH/ft sq. Is this viable?
More typical 40'F conditions here require 11100 BTUH, or 19 BTUH/ft sq - which seems more reasonable and within reach.
Huge help from Brad White last week on heat losses. The question concerns a large, mostly open first floor, to which I have access to joist space in context of basement remodel (building 'man-cave' for teenager/friends/guitars/XBox/etc)
So, about 700 ft sq main floor, with about 579 ft sq available for under-floor install (reduced by cabinetry, up and down stairs, etc). Heat loss for total area 18500 BTUH at design temp of 20'F here in Seattle, or 32 BTUH/ft sq. Is this viable?
More typical 40'F conditions here require 11100 BTUH, or 19 BTUH/ft sq - which seems more reasonable and within reach.
0
Comments
-
what is the floor finish
carpet, for sound absorption? If so, probably not.
with wood, you will technically exceed warranty specs on most wood floors. On a floating floor I wouldn't care about that as long as you used water temperature reset. High temp though.
with tile, no problem.Rob Brown
Designer for Rockport Mechanical
in beautiful Rockport Maine.0 -
Heat Loss...
Your heat loss actually comes to a little over 26 btu's pr. sq. ft. With tubing on 8" centers, you would have 870' of tubing (580 x 1.5). Allowing 20 btu's pr. lineal foot output would give you 17,400 btu's. This is some what conservative, but would also depend on floor coverings, wood thickness, etc. So it should be enough, depending on these variables. 1000btu's isn't enough to make a difference at this size and you could run the water temp slightly higher to compensate.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Floors...
...are mostly hardwood. Sub is 0.5 inch shiplap fir (100yr old), wood is 0.75" Jatoba. Kitchen is cork tile, bath ceramic tile. Vast majority of the area is the jatoba.
Is there a BTUH/FtSq limit for hardwood? Or is it based on water temp?0 -
most MFGs
won't warrantee over 85 degree surface temp which is about 30 BTUs/sq ft.
however in your case if warranty is not a concern you'd probably be fine with the thinner wood (including subfloor).Rob Brown
Designer for Rockport Mechanical
in beautiful Rockport Maine.0 -
thanks!
Yup, around 30 BTUH/FtSq is what I was aiming at, at design temp, and usually much less.0 -
thanks!
I'll go back and check my numbers later this evening0 -
Are these calculations correct?
I'm trying to figure out the input water temp, the delta T, and the flow rate, using the formulas from Modern Hydronic Heating.
If I need to deliver 18000 BTUH and have 580 ft s to do it, that's an upward heat flux of 31 BTUH/ft sq.
Water Temp = Air Temp + q(up) * (Rff + Rair)
If Air Temp=67
Rff=1.31
Rair=0.61
q(up)=31
Water Temp = 127.5 (average)
******************
For flow rate,
BTUH = GPM * delta T * 500
18000 = GPM *10 * 500
GPM = 3.6 (total throughout 4 loops)
******************
Where I'm getting confused...
if q(up) is 31, and q(down) is 3.8, a=0.566
That gives...
b = (a * L) / (500 * F)
= (.566 * 870) / (500 * 3.6)
= 0.274
Outflow Temp is then = Room Temp + (Input Temp - Room Temp)*e^-b
If Room Temp is 67,
Input Temp is 130 (Ave Temp + 0.5*delta T)
then
Outflow Temp = 115
This is what doesn't add up for me:
Ave Temp is 125
Delta T is 10,
but outflow temp is 115 - more consistent with delta T=20 (Is that too high?) and input temp is 135 (is that too high?)
Thanks for everyone's help and patience!!0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements