Towel Warmer hookup
Ablegeorge
Member Posts: 2
I am getting ready to hook up a radiant towel warmer. I am installing valves immediately at the warmer. Where should they go? Both supply and return on bottom or both on top or one on bottom and the other on top?
Thanks for the help
Thanks for the help
0
Comments
-
Supply/Return
They will all work, but having the supply on top, return on the bottom is the most efficient, As the water gives up its heat, it will fall to the bottom of the radiator naturally.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Got TRV????
One of your valves should be a TRV. Someone makes one (Oventrop?) that allows the sensor to hang downwards and not take your knee caps out.
METhere was an error rendering this rich post.