Efficiency rating and sizing of a new gas boiler
Belmont
Member Posts: 1
in Gas Heating
Hi,
1. Is there a formula or standardized process when sizing for a natural gas boiler?
For example, a house with 1850 square feet (that's the current area being
heated) with 2 heating zones (2 thermostats - one on the first floor and one on the
2nd floor). There is additional space in the house that is not heated (i.e. unfinished
attic and basement).
2. Is there a direct relationship between the number of therms used and the efficency
rating of the boiler? For example, if 100 therms are used in one month with
a boiler that has a 70% efficency rating would a boiler with a 95% rating use
only 75 therms for the same period? (In this example I'm assuming all other
factors are the same (i.e. outside temperature, same thermostat settings, same
thermal conversion factor).
Thanks!
1. Is there a formula or standardized process when sizing for a natural gas boiler?
For example, a house with 1850 square feet (that's the current area being
heated) with 2 heating zones (2 thermostats - one on the first floor and one on the
2nd floor). There is additional space in the house that is not heated (i.e. unfinished
attic and basement).
2. Is there a direct relationship between the number of therms used and the efficency
rating of the boiler? For example, if 100 therms are used in one month with
a boiler that has a 70% efficency rating would a boiler with a 95% rating use
only 75 therms for the same period? (In this example I'm assuming all other
factors are the same (i.e. outside temperature, same thermostat settings, same
thermal conversion factor).
Thanks!
0
Comments
-
The best way to determine
is to do an actual heat loss calculation with any one of many procedures for doing the heat loss. It takes into consideration amount of insulation, type of windows, type construction etc. Something Like ASHRAE Manual J or Slant Fin has a program available on the Internet
To answer question #2 there is obviously a direct relation ship to the amount of fuel burned based on a degree day analysis. It then depends on many other factors. Example I could install a very high efficiency boiler on a very inefficient system or building. That would make the boiler in actuality less efficient due to poor system design.
Most legitimate contractors will be able to do an effective analysis ( heat loss) and give you a design that matches your particular needs.
Boilers are advertised with AFUE ratings as to efficiency. Those are sometimes suspect when you do an actual combustion analysis or thermal efficiency calculation.
The decision as to size may also take into consideration the existing system and boiler. Be careful however as in the past many boilers were over sized
You also want to determine the rating of your emitters (baseboard, radiators or convectors).0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements