hvac
tae
Member Posts: 1
i have 8kw strip and only 1 side is heating i have voltage going in and coming out, i have 26amps going in 14amps coming out it is an old trane unit from 1990
0
Comments
-
Not sure...
What your question is, but it sounds like your heat element is split apart and grounded. Not an uncommon failure with spiral elements.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Current in a circuit
If you are measuring the amperage before and after the heaters and are getting measurements of 26A and 14A respectively, you definitaly have a short to ground somewhere. The current being supplied to a circuit from a distribution panel should be the same as the current returning to the distribution panel. If such is not the case, the current is being lost somewhere.
De-energize the circuit, disconnct the power leads to the heaters and check for resistance/continuity to ground.There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 421 Carbon Monoxide Awareness
- 81 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 893 Plumbing
- 5.9K Radiant Heating
- 379 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements