Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
budarus 162/100
Steve_210
Member Posts: 647
budarus 162/100this was installed about 3 months ago. all ok until last night. customer claims fault code on the BC10 was either F08 or F04. I cannot find this in the manual. F is for pump overun time but it does not explain the locking fault. He shut off the power and let reset all ok again. any help greatly appraciated <a href="http://www.heatinghelp.com/forum-reply/1209605/budarus-162-100">Reply</a> <a href="http://www.heatinghelp.com/forum-edit-post/1209605/budarus-162-100">Edit</a>
0
Comments
-
Error Code
Could the customer have mis-read the code? Could he have mistaken the "F05" pump run on for a fault code? Or maybe, he reversed the digits? "4F" = Safety temp sensor exceeded 221 deg. Section 29 & 37 of the service manual.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
thats what i,m thinking
I will see what happens. thanks for the reply.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements