budarus 162/100
Steve_210
Member Posts: 646
budarus 162/100this was installed about 3 months ago. all ok until last night. customer claims fault code on the BC10 was either F08 or F04. I cannot find this in the manual. F is for pump overun time but it does not explain the locking fault. He shut off the power and let reset all ok again. any help greatly appraciated <a href="http://www.heatinghelp.com/forum-reply/1209605/budarus-162-100">Reply</a> <a href="http://www.heatinghelp.com/forum-edit-post/1209605/budarus-162-100">Edit</a>
0
Comments
-
Error Code
Could the customer have mis-read the code? Could he have mistaken the "F05" pump run on for a fault code? Or maybe, he reversed the digits? "4F" = Safety temp sensor exceeded 221 deg. Section 29 & 37 of the service manual.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
thats what i,m thinking
I will see what happens. thanks for the reply.0