I am currently working at a site where they are using the hot water to heat with.This is a large high end condo.there are air handlers and  diverting valves in each unit.The common water is supplied at 180* with a mixing valve to temper the water for potable use.My concerns  are when you are not using the heat the water sits stagnant in heating coil in air handler until you turn it on again,then that whatever temp stagnant water is mixed in with the rest ,so  are  they   brewing legionnaire's in these coils ? i called the state and was told if its existing and i service it i accept no liability , being a licenced plumber i am still concerned  what do you think ?

Comments

  • bob eck
    bob eck Member Posts: 930
    hot water for heating

    if you want to be safe use a plate heat exchanger. run water heater 180* water through one side and run water in the duct coils in the other side.

    the two different waters will never touch.
  • Jamie Hall
    Jamie Hall Member Posts: 24,859
    I'll go with Bob

    and use a heat exchanger to separate the two circuits.



    And I'll add that, while I don't recall the Code exactly (something about time...), I do recall that in another life, somewhere back there, when I was a plumbing etc. inspector, I'd never have permitted mixing heating and domestic water without using a heat exchanger -- and an RPZ backflow valve or air gap for filling the heating circuit.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Open System

    I don't like open systems; not because they are dangerous since I've never heard of a case of Legionnaire's from this and as long as the piping is approved for potable use, I don't believe there's anything in the code to disallow it.  I don't like it because it's usually the low bid.
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,858
    The reason you don't hear about it....

    is because, per the CDC, "It is THE most misdiagnosed disease in the world..." Usually misdiagnosed as "common bacterial pneumonia."



    It happens everyday. All coper systems are less susceptible than PEX systems, but it is still present.



    Every person reading this has been exposed to the bacteria at one point in time or another. It is a matter of concentration of the bacteria, and exposing yourself while your immune system is depressed.



    This has been beat up here ad nauseum by myself and professor Yates,



    Do a site search for legionella pneumophila and se what comes up.



    If I had my way, it would be illegal to do this type of system, and as soon as the lawyers get ahold of it, it will be...



    Just a matter of time.



    ME

    There was an error rendering this rich post.

  • Charlie from wmass
    Charlie from wmass Member Posts: 4,373
    Its illegal in Massachusetts

    Funny how it must only be us that have the bacteria that cause disease. It is legal in Connecticut, New York. New Hampshire, and Vermont. Even if it is legal I would not do it.