short cycle
jtp
Member Posts: 5
i have done some pipe replacement on this system...there were leaks everywhere....Now the system runs up to 2 lbs in about 4 minutes ,shuts down,,,drops to 0 in about 30 seconds and back on......
0
Comments
-
At a guess...
I would say that the venting -- whatever it may be -- on your system is very inadequate. Or simply not working at all. Depending on exactly what kind of system it is, the steam mains or the dry returns need venting -- lots of it. Four minutes to run up to 2 pounds is very very short, and very much suggests either that the vents aren't there or they aren't working.
And 2 pounds is too high a pressure, except for a very few rather unusual systems. The cutin should be around half a pound, max., and the cutout a pound and a half -- max. If you have a vaporstat, you can probably go even lower, again depending on the exact system. 2 pounds may be enough to close and hold closed whatever vents are there on your system, and you'll have very inadequate heat.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements