Steam Pressure
Options
dave_20
Member Posts: 5
I know this is Steam 101 stuff but we don't see much of it around here so I don't get much practice - what should the pressure gauge read on a residential Pennco steam boiler? I had one today that was at zero while running.
0
Comments
-
Sounds about right...
particularly if you are looking at the code 0-30 psi gauge. Most residential steam systems should run less than 2 psi max. -- in fact, most seem to work best in the ounce per square inch range; possibly as high as 1.5 psi cutout/.5 psi cutin. And you won't see that on the code gauge...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
low pressure gauge
you can get a good 0-3 psi low pressure gauge from gaugestore.com and mount it on the same pigtail as the pressuretrol, or better yet vaporstat. that way you know what the pressure is.--nbc0 -
Thanks guys, and..
..I've seen them show a vacuum. Why?0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements