Steam Pressure
dave_20
Member Posts: 5
I know this is Steam 101 stuff but we don't see much of it around here so I don't get much practice - what should the pressure gauge read on a residential Pennco steam boiler? I had one today that was at zero while running.
0
Comments
-
Sounds about right...
particularly if you are looking at the code 0-30 psi gauge. Most residential steam systems should run less than 2 psi max. -- in fact, most seem to work best in the ounce per square inch range; possibly as high as 1.5 psi cutout/.5 psi cutin. And you won't see that on the code gauge...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
low pressure gauge
you can get a good 0-3 psi low pressure gauge from gaugestore.com and mount it on the same pigtail as the pressuretrol, or better yet vaporstat. that way you know what the pressure is.--nbc0 -
Thanks guys, and..
..I've seen them show a vacuum. Why?0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements