Gravity furnace not turning on

I had this problem sporadically last year, but this year after initially turning on, my gravity furnace is not firing up.  The pilot is lit and the connections from my Honeywell Powerpile thermostat to the furnace appear to be sound.  Any thoughts?

Comments

  • Tim McElwain
    Tim McElwain Member Posts: 4,641
    Do you have

    a multimeter with a millivolt scale on it? If so I will send you a procedure for testing the system if you e-mail me at gastc@cox.net .
  • Tim McElwain
    Tim McElwain Member Posts: 4,641
    Powerpile testing procedure

    is in the mail. Feel free to call me if you have any questions. 401-437-0557
  • Al_11
    Al_11 Member Posts: 34
    gas valve

    It doesn't take much to stick a millivolt gas valve, it it does not come on hit it with a wrench, it it comes on, replace the valve

    Al
  • Tim McElwain
    Tim McElwain Member Posts: 4,641
    That is not very sound

    advice Al. There is a correct procedure for properly diagnosing a powerpile problem.
  • Empire_2
    Empire_2 Member Posts: 2,340
    I agree with Tim

    Powerpile generator must have a consistent pilot flame to ensure the correct mv. reading at gas valve.  Using a meter will verify this.  You could have a safety switch with corroded contacts.......but if you change the valve, you will find out the hard way.  It's always good to use proper test procedures if for nothing else to learn trouble shooting skills.



    Mike T.