Master trapping

Steve_210
Member Posts: 647
Got a call yesterday to go to an apartment building with 1 radiator not working (at least that's what they are saying). Disconnected supply and return - the thermostatic element in the trap was totally sheared off, from I presume water hammer. In the basement there has been a new boiler installed with a condensate pump and an F& T master trap (I know this is incorrect) I am going to have some problem convincing the owner that they are going to have to replace all the traps on all the radiators in the building. They are going to ask me - how come it worked for the last 3 years? (This is when the master trap was installed - I believe). I just want to get an opinion on if what I am going to say is correct. As more and more of the traps failed, you started to loose pressure differential between the supply and return, and the smaller supply and return risers are the ones going to get affected first. The longer this goes on the more radiators will not work and the more uneven the heat will be in the building. There is no quick fix - the only answer is to change all the radiator traps in the building. If I can find replacement elements for the traps I can also replace those.
Thanks for any help
Thanks for any help
0
Comments
-
They aren't going to like you
but it sounds to me as though you are very much going the right way -- master trapping, as it says in the gospel according to Dan, is going to kill you -- if not now, later, as traps fail around the building! And I would agree on your diagnosis, too -- that it can be a progressive thing, as you are seeing.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Trap Parts
Here's a couple of links if you need trap parts.
Hoffman: [url=http://www.bellgossett.com/literature/files/7262.pdf]http://www.bellgossett.com/literature/files/7262.pdf
Tunstall: [url=http://www.tunstall-inc.com/tunstallsteam.html]http://www.tunstall-inc.com/tunstallsteam.html0 -
Master trapping
thanks guys it would be intresting to see if any contractors have had similar proublems and how best to approach the building owners.0 -
Tell them
you're either going to do it right, or not at all. If they tell you trap rebuilds are too expensive- walk. It's that simple.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
thank you
thanks to everybody. looks like we will be replacing all the elements0 -
Thermal Imaging
Do you know anybody with a thermal Imaging camera? I saw one used last month and they would be great for spotting bad traps on a big job.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements