Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Boiler won't stay lit
BP3
Member Posts: 7
in Gas Heating
It's Sunday and my Raypak boiler HSI igniter is inop. I tried to manually light it to heat up some water for showers etc, but the burner won't stay lit. I checked the igniter and it is open. Does the igniter need to be in the circuit and have continuity for it to stay lit?
0
Comments
-
I believe
the ignitor is also the flame sensor. So it has to be working.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
The igniter will
have to be replaced. The system will not work without it being able to sense the flame.
Even if a seperate flame sensor is used it will only work for one cycle, you would have to keep relighting it on every call.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements