Boiler won't stay lit
BP3
Member Posts: 7
in Gas Heating
It's Sunday and my Raypak boiler HSI igniter is inop. I tried to manually light it to heat up some water for showers etc, but the burner won't stay lit. I checked the igniter and it is open. Does the igniter need to be in the circuit and have continuity for it to stay lit?
0
Comments
-
I believe
the ignitor is also the flame sensor. So it has to be working.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
The igniter will
have to be replaced. The system will not work without it being able to sense the flame.
Even if a seperate flame sensor is used it will only work for one cycle, you would have to keep relighting it on every call.0