Need 2 boilers?
            
                
                    Timco                
                
                    Member Posts: 3,040                
            
                        
            
                    I am finally re-piping the boiler I posted a while back. Question is can the main new boiler be made to make the hot water as well? There is a small Bryant steamer that makes the DHW through a small HX. Can I axe that small unit and use the big dog to heat and make the DHW with steam or do I need to pull hot water from the steamer and use that for the domestic? I will worry about sizes after I figure out how to do this. Small Bryant needs attention as it has a real hard start and I would like to get rid of it before considering replacing it.
Tim
                Tim
Just a guy running some pipes. 
0                
            Comments
- 
            Need 2 boilers
Hello.
Some of the manufactures makes steam boilers with tankless water heaters, they are have to be special order res. I did include file for Weil McLain EGH Steam Boiler with build-in tankless heater option, look on page 18.
VictorThere was an error rendering this rich post.
0 - 
            GB300
The Smith GB300 stays, and is being re-piped to add a hartford loop and a real header. More on that later...
TimJust a guy running some pipes.0 - 
            hot water from steam boiler
does the smith have enough reserve capacity, beyond the needs of the radiators and piping for making hot water? a hotel probably has larger hot water needs than say an apartment building-especially if they have a restaurant, and do their own linen washing.
is the dhw boiler completely shot? i would do some calculations of hot water consumption, before removing it. it could be junked later when you know it is not needed. i would think there could be some advantages in keeping dhw production separate from heating in a heavy use situation. so just "slide it out of the way" until you are certain it won't be needed!--nbc0 - 
            copper fin tube to the rescue
Why not use one of the fin tube units inplace of the bryant? Size it to the load and be done with it. I am talk something like an A.O. Smith water heater. with an insulated storage tank.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 - 
            Smith boiler
The Smith unit is 11 sections and likely way bigger than needed. 40 units, 3-4 rads per unit. Already sitting there, owner wants to use it, period.As for the DHW, I left the printout on site but it was firing at 1500+ppm CO. I clean it today, vent and all, and pour the pad for the Smith unit. I LOVE this job! The other building has an Ajax boiler that is high pressure, no HX.
TimJust a guy running some pipes.0 - 
            how new is the smith?
I was thinking if it is way to big can you remove a section or 2 and bring it down to size? the shorter manifold could be purchased from smith. Just a thought. or do as the old timers did and remove and plug an orfice or 2. I have seen some way over sized units where 4 orfices were removed and plugged so the boiler the engineer speced did not steam the building into outer space. The 30% rule gets used a lot.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 
This discussion has been closed.
            Categories
- All Categories
 - 87.2K THE MAIN WALL
 - 3.2K A-C, Heat Pumps & Refrigeration
 - 59 Biomass
 - 427 Carbon Monoxide Awareness
 - 118 Chimneys & Flues
 - 2.1K Domestic Hot Water
 - 5.7K Gas Heating
 - 113 Geothermal
 - 164 Indoor-Air Quality
 - 3.7K Oil Heating
 - 73 Pipe Deterioration
 - 1K Plumbing
 - 6.4K Radiant Heating
 - 393 Solar
 - 15.5K Strictly Steam
 - 3.4K Thermostats and Controls
 - 56 Water Quality
 - 51 Industry Classes
 - 49 Job Opportunities
 - 18 Recall Announcements
 