steam systems
I'm replacing a large water volume fire tube boiler with a cast iron sectional boiler with less water content. It is a one pipe system and will be cost prohibitive to trap the ends of the mains and install a make up water tank. Any ideas?
  • nugs
    nugs Posts: 77
    need more info on what was what and what will be.
    In the mean time take a look at Everhot's site under steam condensate tank. It is a tank that mounts on the steam outlet and gives you more room to make steam off the top of the boiler, It also has a separator that keeps wet steam from entering the main. Not sure if they make one big enough for your application though.
  • J.C.A._3
    J.C.A._3 Posts: 2,980
    Well,
    How big are we talking here? That, and what is it heating ? C.
    Jamie Hall Posts: 27,862
    Seems to me...
    that I'm guessing that your concern is that you'll generate a lot of steam and it will take time for the condensate to return, and in the meantime the water level will drop too low?
    Just how big a system is this we're talking about here? In general unless it's a really really big system in terms of pipe and radiation volume, or your pressure is really high (I hope not!) the volume of steam required to completely fill the system is going to be so much less than the volume of water in the boiler -- even in one of the newer sectionals -- that you won't have a problem. Remember that steam occupies over 1,000 times the volume of water from which it is made!
    Need more info...
  • I agree with Jamie
    If the boiler is sized to the connected load , there really should not be a need for any add ons ( like a condensate or reservoir tank ) . And if the header is sized and piped correct , there is no need for an external tank up there to lower the velocity of the steam .
