Could you provide me with the latest information concerning modular boiler systems to replace existing single gas fired boilers with a millon btu or more.Info on boilers and design would be of most interst, thank you in advance, RJ
  • Why not consider...
    4 399 mod cons would probably fit into the same space (stacked) as the million btuH fire breathing dragon. 4 units cascaded would give you a 20:1 turn down ratio...
    Dang near infinite:-)
    ME
  • Brad White
    Brad White Member Posts: 2,399
    Or
    Hydrotherm KN-6's, KN-10's
    Buderus, Viessmann, Cleaver-Brooks... they all make boilers in that size range. When you say "modular" I take it you mean multiple boilers, not that they have to align in a monolithic block.
    "If you do not know the answer, say, "I do not know the answer", and you will be correct!"
    -Ernie White, my Dad
  • And...
    What makes you so sure you need to replace the EXACT btu's on site? If the boiler has been doing DHW through a side arm heat exchanger, chances are you can CONSIDERABLY down size the heat source, provided you can add some storage to the DHW mix.
    For example, it is not uncommon for us to eliminate a 1,500,000 btuH boiler with a side arm, and replace it with two 300K boilers and 160 gallons of DHW capacity.
    As a matter of fact, we wil be perfoming that exact feat this Tuesday... All hands on deck!
    Suggest a heat loss calc be done on the skin of the building, followed up with a sample room by room audit of emmiter versus load, and proper sizing done on the DHW load. I think you will be suprised by the results....