System Sketch
Mike T., Swampeast MO
Member Posts: 6,928
<U><B>TACO 006 - Circulator</B></U>
19,000 mbh Manual-J for 2,400 sq.ft. @ -20F.
<U>3/8" branch piping.</U>
Fully TRVd, two-pipe system using 15 emitters and 14 circuits.
11,000 btu/hr (60% <I>heat requirement</I> assumed at design)
<B>5F delta-t @ 130F = 4 gpm @ 6.6' head (2.3 psi)</B> <I>with insignificant bypass</I>.
Differential pressure bypass valve setting = 6' (2.2 psi)
Approx. 4 gpm @ 6' head <I>constant</I> system flow.
130F <B>FIXED</B> supply temperature.
5F delta-t
5F delta-t
Can any reasonable installer follow?
The 4' at each end of the floor trusses is open with solid web connecting.
large (3.3 meg) file0 -
give me more head, delta-t and flow
typical winter flow
9,000 btu emitter output
8°F delta-t ----- [ increasing with supply temp above 130°F ]
2¼ gpm emitter flow + 1¾ gpm bypass flow @ 6½' (2.25 psi) --- [ emitter flow decreasing with increasing delta-t and increasing supply temp ]
Sketch Has Been Cropped
reload for better view0 -
Am I missing something Mike?
is this some sort of test? Given the impeccable knowledge you`ve shown in the past here, can`t you do the math?
Dave0
- 109 Chimneys & Flues
- 5.6K Gas Heating
- 970 Plumbing
- 386 Solar
