Flow check vs Zone Valve on radiant system
        
            Options        
            
        
 
            
                
                    Steve Garson                
                
                    Member Posts: 191                
            
                        
            
                    The flow check on my radiant system doesn't really stop convection.  As a result, my floors get some heat when they shouldn't.  The convection of the hot water runs against the flow-check.  I opened the valve and cleaned it carefully.  I even replaced the Taco inner parts with a new one.
It isn't practical to install another one on the other end of the loop since it would be close to impossible to properly drain that pipe to be able to sweat it properly.
Is there any reason I shouldn't just replace the Taco flow-check with a Taco zone valve that simply will shut closed when the circulator is off?
Thanks,
Steve
Boston
                It isn't practical to install another one on the other end of the loop since it would be close to impossible to properly drain that pipe to be able to sweat it properly.
Is there any reason I shouldn't just replace the Taco flow-check with a Taco zone valve that simply will shut closed when the circulator is off?
Thanks,
Steve
Boston
0                
            Comments
- 
            
 I used taco flo checks on my system, and found out the hard way they are for horizontal installation only. If that is not the problem, you may need checks on the return, as hot water rises, and I had zones heat up slowly from that fact. (HW ghosting up through the zones not in use through the returns.) My local B&G dealer got me into some center spring silent check valves that threaded right in. I have had no problems since putting them on both sides.
 TJust a guy running some pipes.0
- 
            
 I have it installed horizontally.0
- 
            gravity flow
 you may have got some solder on the seat.which would prevent a tight seal. i prefer screw type for some valves & equipment for that reason. you could put a heat sink or spring check on the return.0
- 
            I've come to prefer zone valves
 for this. Works every time. Where applicable however, use one of those new circs with spring check. Cheaper and works well.0
- 
            Check valves less expensive
 Check valves either integral or external will help with ghost flow. However, only .4 psi is required to open a check so when designing the system you should be certain not to create a pressure drop greater, because of ghost flow. You may need a check on the supply, and return, or if you can not stop the migration of flow, you can always install the flow control zone valve
 Taco, Inc.
 Joe Mattiello
 Technical Service Technician
 joemat@taco-hvac.com
 401-942-8000 X 484
 www.taco-hvac.comJoe Mattiello
 N. E. Regional Manger, Commercial Products
 Taco Comfort Solutions0
This discussion has been closed.
            Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 118 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 112 Geothermal
- 164 Indoor-Air Quality
- 3.7K Oil Heating
- 73 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements