Flow check vs Zone Valve on radiant system

Steve Garson
Steve Garson Member Posts: 191
The flow check on my radiant system doesn't really stop convection. As a result, my floors get some heat when they shouldn't. The convection of the hot water runs against the flow-check. I opened the valve and cleaned it carefully. I even replaced the Taco inner parts with a new one.

It isn't practical to install another one on the other end of the loop since it would be close to impossible to properly drain that pipe to be able to sweat it properly.

Is there any reason I shouldn't just replace the Taco flow-check with a Taco zone valve that simply will shut closed when the circulator is off?

Thanks,

Steve
Boston

Comments

  • Timco
    Timco Member Posts: 3,040


    I used taco flo checks on my system, and found out the hard way they are for horizontal installation only. If that is not the problem, you may need checks on the return, as hot water rises, and I had zones heat up slowly from that fact. (HW ghosting up through the zones not in use through the returns.) My local B&G dealer got me into some center spring silent check valves that threaded right in. I have had no problems since putting them on both sides.

    T
    Just a guy running some pipes.
  • Steve Garson
    Steve Garson Member Posts: 191


    I have it installed horizontally.
  • bob young
    bob young Member Posts: 2,177
    gravity flow

    you may have got some solder on the seat.which would prevent a tight seal. i prefer screw type for some valves & equipment for that reason. you could put a heat sink or spring check on the return.
  • bill clinton_3
    bill clinton_3 Member Posts: 111
    I've come to prefer zone valves

    for this. Works every time. Where applicable however, use one of those new circs with spring check. Cheaper and works well.
  • Joe Mattiello
    Joe Mattiello Member Posts: 720
    Check valves less expensive

    Check valves either integral or external will help with ghost flow. However, only .4 psi is required to open a check so when designing the system you should be certain not to create a pressure drop greater, because of ghost flow. You may need a check on the supply, and return, or if you can not stop the migration of flow, you can always install the flow control zone valve