Buderus GB 142 and Argo ARM4P
carol_3
Member Posts: 397
Here's what my friend Dennis Bellanti says:
The terminals on the Buderus that are considered T-T are actually W-A. A dry contact switch can be wired here. No powered contacts allowed! If he is going to use W&A terminals then he should not use the RC10 which is the room controller that is provided with the boiler. You can only use one or the other, not both
Buderus GB142 w/Argo ARM4P
I've just about completed the instalation of a Buderus GB142-30 and I'm getting ready to wire up the circulators. The Buderus manual wants it's TT conection wired to the XX conections on the switching relay (Argo ARM4P) and I'm not sure if the are refering to the XX conections on the botom row of conections on the Argo. These (XX) are on the same bus with the circulator terminals, but appear to have 24V transformers. ??? Don't want to blow the circuit board on the Buderus.0 -
I'll see if I can dig something up. How about you Buderus guys?0 -
XX terminals
on the switching relay are a dry set of contacts. Just a switch that closes on a call for heat.
Mark H
GB142
I forget to check this section, Sorry!
The "WA" terminals on the GB142 are for the end switch connection from a multizone or single zone thermostat. The end switch must be a dry set of contacts! If the RC10 is being used it would be wired into the "RC" terminal. Either the RC10 is connected or the end switch, but not both. Thanks0
- 117 Geothermal