Pressurtrol Question
Options
superMARKet
Member Posts: 87
"B" controls make contact on pressure rise, and then open again whent he pressure falls. This is usually the opposite of what you want on a boiler where you're using the pressuretrol to control the burner. You want the burner to run when the pressure is low, and break contact when the pressure rises past the setpoint. That's what the "A" controls do.
The "B" is more suited to maintaining a minimum, the "A" is for maintaining a maximum.
The "B" is more suited to maintaining a minimum, the "A" is for maintaining a maximum.
0
Comments
-
What is the differnce between a Honeywell PA404A and a PA404B?0 -
The difference
"B" controls make contact on pressure rise, and then open again whent he pressure falls. This is usually the opposite of what you want on a boiler where you're using the pressuretrol to control the burner. You want the burner to run when the pressure is low, and break contact when the pressure rises past the setpoint. That's what the "A" controls do.
The "B" is more suited to maintaining a minimum, the "A" is for maintaining a maximum.0
This discussion has been closed.
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 120 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 394 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements