info on diverter valves
I am looking for a one-in, two-pipe out, and yes, there are two circulators running.
  • GB in Buffalo MN
    GB in Buffalo MN Member Posts: 6
    I just read Dan's book on primary/secondary piping. I need help on finding and understanding diverter valves. This is for a radiant floor system - 140F in, 4 GPM total flow, 100F design @ 15F delta T. 3.1 GPM bypass (24,500 btu load)
    Thanks
  • Brad White_9
    Brad White_9 Member Posts: 2,440
    Diverter or Mixing?
    Typically, a diverter valve goes on the discharge (outlet) side of a circulator. One in-port, two out-ports. Thus applied, they cannot affect temperature unless another downstream circulator is involved.
    A mixing valve is typically on the suction (inlet) side of a circulator, with two in-ports and one common out-port passing the mixed temperature.
    ESBE (Danfoss), Tekmar, Oventrop, Viessmann and others all make or market such valves and have literature which will help you select them appropriately.
  • ALH_4
    ALH_4 Member Posts: 1,790
    TV
    Are you talking about these? Thermic Valves
    They are built specifically for boiler protection.