info on diverter valves

GB in Buffalo MN
Member Posts: 6
I am looking for a one-in, two-pipe out, and yes, there are two circulators running.
0
Comments
-
info on diverter valves
I just read Dan's book on primary/secondary piping. I need help on finding and understanding diverter valves. This is for a radiant floor system - 140F in, 4 GPM total flow, 100F design @ 15F delta T. 3.1 GPM bypass (24,500 btu load)
Thanks0 -
Diverter or Mixing?
Typically, a diverter valve goes on the discharge (outlet) side of a circulator. One in-port, two out-ports. Thus applied, they cannot affect temperature unless another downstream circulator is involved.
A mixing valve is typically on the suction (inlet) side of a circulator, with two in-ports and one common out-port passing the mixed temperature.
ESBE (Danfoss), Tekmar, Oventrop, Viessmann and others all make or market such valves and have literature which will help you select them appropriately.0 -
0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 942 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements