Down Zoning
Xc8p2dC_2
Member Posts: 150
Asked this question before , but got buried. Now a member of Pink Floyd Nation, so thought I would ask again
Can a small 2 Zome [TACO] 4x oversized natgas boiler with fintube and 1 Cirulator [on the return side] be effectively switch to only ONE large zone by utilizing 1 Tstat and slaving the zone valves together and eliminating one of the TT to the A-S control
TIA
TIA
yes
You disconnect one of the thermostats, and leave one of the valve in the manual position, so when ever the thermostat calls for heat hot water will flow to both zones.
Joe Mattiello
Technical Support Technician
Tel. 401-942-8000 X 484
Fax. 401-942-2360
1160 Cranston St
Cranston, RI 02920
joemat@taco-hvac.com0 -
Thanks Joe
I thought about that, but figured it was too easy
I don't have any weighted check V's, so wasn't sure if I would have backflow issues0
- 167 Indoor-Air Quality