Using cast iron baseboard for steam?
Options
Brad White_9
Member Posts: 2,440
I think the limit with one pipe steam anyway, is about ten feet. Not sure if having two-pipe makes a difference.
0
Comments
-
Using cast iron baseboard for steam?
Can I use cast iron baseboard in a two pipe steam system? If so is there a limit in the lenght of each piece of baseboard? We will have a valve on one side and a steam trap on the other. Thank you.0 -
yes...
Burnham: http://www.burnham.com/lit/Baseray4-04.pdf
Weil-McLain: http://www.weil-mclain.com/downloads/literature/baseboard/snug.pdf
are 2 choices0 -
I new I could do it ,my question was more about max lenghts or if there is a lenght limit for steam?0 -
CIBB for steam
Try to limit them to 6 ft. lengths, although I have seen them longer, but if vented too fast the longer ones usually hammer.
Dave0 -
max length on cast iron baseboard
Hi Jason,
As with a lot of questions, the answer is yes, no, maybe and sometimes.
yes - cast iron baseboard is rated for steam use, one or two pipe
no - You can have problems trying to mix it into a system that has standing cast iron radiators. It has been my experience that when mixing steam radiation types (standing cast and cast baseboard) the max length on a two pipe system is about 6-8 feet to maintain even heat in the home. This usually presents a piping or economic issue. If the cast baseboard is on a different zone than the standing cast, then size the base for the heatloss, but residential steam is rarely zoned. The over 8 ft. cast base tends to take longer to heat vs. standing cast, therefore the room(s) with the cast base lose temperature.
maybe and sometimes - see above
Best regards, Pat0
This discussion has been closed.
Categories
- All Categories
- 87.5K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 429 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 119 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 394 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 50 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements