Using cast iron baseboard for steam?
Brad White_9
Brad White_9 Member Posts: 2,440
I think the limit with one pipe steam anyway, is about ten feet. Not sure if having two-pipe makes a difference.
  • Jason_22
    Jason_22 Member Posts: 39
    Can I use cast iron baseboard in a two pipe steam system? If so is there a limit in the lenght of each piece of baseboard? We will have a valve on one side and a steam trap on the other. Thank you.
  • Jason_22
    I new I could do it ,my question was more about max lenghts or if there is a lenght limit for steam?
  • CIBB for steam
    Try to limit them to 6 ft. lengths, although I have seen them longer, but if vented too fast the longer ones usually hammer.
    Dave
  • max length on cast iron baseboard
    Hi Jason,
    As with a lot of questions, the answer is yes, no, maybe and sometimes.
    yes - cast iron baseboard is rated for steam use, one or two pipe
    no - You can have problems trying to mix it into a system that has standing cast iron radiators. It has been my experience that when mixing steam radiation types (standing cast and cast baseboard) the max length on a two pipe system is about 6-8 feet to maintain even heat in the home. This usually presents a piping or economic issue. If the cast baseboard is on a different zone than the standing cast, then size the base for the heatloss, but residential steam is rarely zoned. The over 8 ft. cast base tends to take longer to heat vs. standing cast, therefore the room(s) with the cast base lose temperature.
    maybe and sometimes - see above
    Best regards, Pat