costing her money
Brad White
Member Posts: 2,399
http://www.heatinghelp.com/newsletter.cfm?Id=77
Sometimes it pays to Bounce off the Wall :)
"If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad
radiator decorative covers
I just completed a boiler install for a friend. She insists on leaving some decorative covers on a few of her radiators. On some others she has placed shelves with knik-knaks for decoration.
My question is, is this killing the heating efficiency of the system. I tell her it is but dont't have any reference to make a compelling argument.
A normal boiler install for me would be a 50k lbs steam/hr unit. A Laars 125k btu is a little out of my league.
Input on this subject from a residential professional would be much appreciated.0 -
The newsletter is helpful. The particular covers she is using are the worst case according to the diagrams (add 30%). If a cover open in front but solid on top requires 30% more radiation with a 3" gap between radiator and top, it would seem that a cover sitting directly on the radiator (shelves) would be much worse.
Is this restricted heat radiating through the outside wall?0 -
Look at the second rad cover article
it has the math figured backwards to show the effect of a cover on the existing radiator. In the case of her covers it would reduce the rad's output 33%.