h.w. recirculating with an indirect
kevin coppinger_4
Member Posts: 2,124
valve needs to have check valves installed on it to keep the water from short cycleing through the valve....also And more importantly the T&P balve is NOT installed right...it MUST be w/ in the top 6" of the water heater to sence overheating...unless that probe is 14" long w/ I don't think that exists... very important.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=323&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
recirculating hw with an indirect
have a tt tube smart 80 indirect,witha prestige 110 boiler,indirect set up with califfe mixing valve tank temp set to 150 cw approx 45 and mixed water set to 120. just installed a lainge recirc pump into aux port on tank with dip tube.pump set on timer to run few hrs in morning and evening. water is recic from farthest fixture on second floor via 1/2" line. problem is the 150 degree water is been drawn thru caleffi and to all fixtures whenever pump is running,water tempers back to 120 after fixture is open for a few minutes.what is proper piping to avoid this potential scald issue,see pictures for present piping thanks0 -
What model is it?
Looks like a Zurn.
Tim
RECIRC
ck valves where ,between caleffi and what sorry don't understand youranswer, i'm thinking i have to draw the cold water as well as hot (150) tank water thru caleffi to get proper mixing while pump is recircing or do i return ricirc line to a tee upstream of caleffi valve. t & p is at hottest water location0 -
the t&p may..
be in the hottest pipe location but NOT in the tank...it must be in the tank, by code, look at the install instructions.
recirc
there is no tapped port on tt tube smart 80 for threading in a t/p valve directly into tank0 -
install tee on top of tank
put the TP valve in top with element hanging into tank and run water out of the branch of the tee0 -
recirc
ok but any ideas on how to recirc w/o drawing the 150 water to the farthest fixture when the pump is runnning0 -
recirc
would installing a 1/2 tee on suction side of lainge recirc pump and conecting to to a tee just below 1" cw tee to caleffi valve create a equal pressure drop across vave and allow the valve to maintain the 120 set point while recircing just thinking an ideas0 -
You could
always just let the loop run wild and mix down at the point of use.What the hell...its all money out the window.0 -
here is a suggestion....
go to the Weil-Mclain website...look at the piping diagram they have for the Gold plus indirect..(it is the same water heater that you have except in W-Mc jacket) Go to page 23 on the install manual....it shows how to pipe it the proper way...and you are correct . The water is not getting equal pressure through the valve.
www.wei-mclain.com/downloads/literature/indirect/goldplusmanual.pdf
One more pic please...
Do you have a pic showing the directional arrow on the recirc? I don't see a flow check, does the circ have one built-in?
Nice curves on the mixed! Likes great!0 -
recirc
thanks kevin i will repipe like the drawing on weil's website and let you know,thank for the info0
- 87.7K THE MAIN WALL
- 127 Chimneys & Flues
- 121 Geothermal
- 79 Pipe Deterioration
- 396 Solar
- 17 Recall Announcements
