Should the circulating pump on the boiler be on the feed line or
Buckeye
Buckeye Member Posts: 11
on the feed line of a hot water boiler or on the return line?
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,574
    On the supply
    Pumping away from the PONPC. If it's existing job I find i much easier to move the Extrol rather than the circulator. As long as you are pumping away from extrol is the main thing.
  • Brad White_9
    Brad White_9 Member Posts: 2,440
    Robert is right
    I agree 100%.
    The best of both worlds is to have the air separator and expansion tank at the outlet of the boiler just upstream of the circulator. Absent that, as Robert said, move the expansion tank to the suction-side of the circulator, no matter where it is. That will take care of 85% of the issues related to air removal and ongoing venting...
  • John Ketterman
    John Ketterman Member Posts: 187
    > I agree 100%.