Should the circulating pump on the boiler be on the feed line or
Buckeye
Member Posts: 11
on the feed line of a hot water boiler or on the return line?
0
Comments
-
On the supply
Pumping away from the PONPC. If it's existing job I find i much easier to move the Extrol rather than the circulator. As long as you are pumping away from extrol is the main thing.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
Robert is right
I agree 100%.
The best of both worlds is to have the air separator and expansion tank at the outlet of the boiler just upstream of the circulator. Absent that, as Robert said, move the expansion tank to the suction-side of the circulator, no matter where it is. That will take care of 85% of the issues related to air removal and ongoing venting...0 -
> I agree 100%.
>
> The best of both worlds is to
> have the air separator and expansion tank at the
> outlet of the boiler just upstream of the
> circulator. Absent that, as Robert said, move the
> expansion tank to the suction-side of the
> circulator, no matter where it is. That will take
> care of 85% of the issues related to air removal
> and ongoing venting...
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements