indirect fired heater temperature pressure relief

Options
Brad White_9
Brad White_9 Member Posts: 2,440
The typical 150 PSI/210F T&P valve is what I would use. Just make sure the BTU rating meets or exceeds the boiler rating. Commonly available item. (EDIT- Yes, ASME as Paul mentioned. I do that reflexively but forgot that many commercial valves are not so rated.Thanks Paul.)